Post by gstan » 25 Mar 2016, 04:21

Hi Sir,

My customer want to have a fixture which is save the ID user who change the set point value

Case 1
Progress,
1.Operator key in his name.
2.Operator key in set value (temperature,time) for product A, CMC start function as controller and record data.
3.Process end, another Operator come to key in set value (temperature,time) for product B, CMC start function as controller and record data.
4. Process keep recycle using same method.

Requirement,
1.Customer want to know who key in the set value (temperature,time), and data been record (including the name of operator key in).
2.If possible, name of operator show in letter (A-Z,exp~John).
3.Assume operator is more than 100 person.

Is it CMC able to do this fixture?
Please advise on how to make it if possible to do this.Thanks.

Case 2
If case 1 cannot be done, we here try to use another device ( exp, PLC,touch screen ) to link with CMC recorder for the username key in.
Progress,
1.Operator key in his name on Touch Screen.
2.Operator key in set value (temperature,time) for product A on a Touch Screen, CMC receive signal thru Modbus, CMC start function as controller and record data.
3.Process end, another Operator come to key in set value (temperature,time) for product B on a Touch Screen, CMC receive signal thru Modbus,, CMC start function as controller and record data.
4.Process keep recycle using same method.

Requirement,
1.After operator key in name (exp~John) on Touch Screen, a channel on CMC show his name [John].
note: every different username also show in this channel.
2.Record the data for it.

Is it CMC able to do this fixture?
Please advise on how to make it if possible to do this.Thanks.

Kindly reply ASAP because it is in urgent.

Thanks you for advise on this.
Best regards,
GS TAN

User avatar
multicon24
Administrator
Posts: 164
Joined: 24 Oct 2012, 20:59

Re: Save the name who is using different ID

Post by multicon24 » 25 Mar 2016, 09:13

Dear Gs Tan,

Case 1 is not possible without additional device.

Case 2 is possible, but CMC is designed to work with numbers. It can't read letters via Modbus. In DAQ Manager, in logged data you'll see numbers. For example "1" might mean John, "2": Tom, etc.

External device, (for eg. PLC) can receive IDs via touch screen or using barcode reader.

--
MultiCon technical specialist
Maciej Mitura

gstan
Posts: 51
Joined: 20 Oct 2014, 09:38

Re: Save the name who is using different ID

Post by gstan » 28 Mar 2016, 04:12

Hi Sir,

Thanks for the prompt reply.

Best regards,
GS TAN