reWrite Hi Lo limit for CMC-99 via ETU modbus

Share your knowledge on how to use equipment MultiCon
Post Reply
haitham Sungkar
Posts: 15
Joined: 13 Jul 2013, 05:51

reWrite Hi Lo limit for CMC-99 via ETU modbus

Post by haitham Sungkar » 22 Jul 2013, 10:25

Dear Multicon,

Now, what about if I would use two separate Logical channel as set point for Hi and Low limit.
We could write the set-point through ETU modbus right?
If yes, then we could set the Hi and Lo limit remotely via ETU. :roll:

please advice. :?:

User avatar
multicon24
Administrator
Posts: 164
Joined: 24 Oct 2012, 20:59

Re: reWrite Hi Lo limit for CMC-99 via ETU modbus

Post by multicon24 » 23 Jul 2013, 06:59

Dear Haitham Sungkar,

Can you explain your idea more precisely?
If you wish to set logical channel value remotely, without using Xming, you can use Modbus RTU protocol. MultiCon CMC will be a Slave, PC with dedicated software will be a Modbus RTU Master. Please take into consideration that you have to use RS-485 instead Ethernet connection. RS-485 is avialable on power supply slot. There is no need to have ETU or ACM card.

--
MultiCon technical specialist
Wiktor Fikier

haitham Sungkar
Posts: 15
Joined: 13 Jul 2013, 05:51

Re: reWrite Hi Lo limit for CMC-99 via ETU modbus

Post by haitham Sungkar » 24 Jul 2013, 00:05

Dear Wiktor,

that's right.
We gonna set logical channel value remotely without Xming (remote display mode).
We've to built one software for monitoring as well as Temperature setting. Because they (the user) don't want to confuse using multiple software.

do you mean that, it can not be done from Ethernet (ETU)?
I know that we could use the built in RS-485. but the customer don't want to invest a long cable for new networking device. instead, they will use an existing Ethernet cable (RJ-45 plug) on site.

User avatar
multicon24
Administrator
Posts: 164
Joined: 24 Oct 2012, 20:59

Re: reWrite Hi Lo limit for CMC-99 via ETU modbus

Post by multicon24 » 26 Jul 2013, 06:22

Dear Haitham Sungkar,

It can not been done from Ethernet ETU. Modbus RTU is implemented with RS-485 slots only.


--
MultiCon technical specialist
Wiktor Fikier

haitham Sungkar
Posts: 15
Joined: 13 Jul 2013, 05:51

Re: reWrite Hi Lo limit for CMC-99 via ETU modbus

Post by haitham Sungkar » 28 Jul 2013, 01:26

Hi Wiktor,

Doesn't it?

what about Modbus TCP Protocol. Multicon CMC has Modbus TCP Protocol, doesn't it?

User avatar
multicon24
Administrator
Posts: 164
Joined: 24 Oct 2012, 20:59

Re: reWrite Hi Lo limit for CMC-99 via ETU modbus

Post by multicon24 » 30 Jul 2013, 11:27

Dear Haitham Sungkar,

1. You can read from and send values to logical channels using Modbus RTU with RS-485 connection,

2. If you wish to read a variable (value from logical channel) only from MultiCon, you can also use both Modbus TCP or HTTP protocol methods. If you wish to download logged data file from the device, it can be done using HTTP protocol only. Modbus TCP doesn't support file transfering.
We suggest, to enter internal CMC web page ( http://<IP_OF_YOUR_CMC>/NetworkInterfaceDescription.html), there you can find few examples and description how to download data file from CMC using HTTP protocol.

3. To send a variable value directly to any logical channel, Modbus TCP protocol can be used. Logical channel has to be set as Modbus Slave mode. Modbus TCP is required to send a data value to CMC, but java applets are not required to do this.


To become more familiar with ModbusTCP please visit :
http://code.google.com/p/phpmodbus/
http://www.phpclasses.org/package/377-P ... kage-.html

If you have more questions, don't hesitate to contact us.


--
MultiCon technical specialist
Wiktor Fikier